if you have heishamon paralel to taw, you could enable hex dump in heishamon and share log while pressing that button in cloud.. |
Beta Was this translation helpful? Give feedback.
All reactions
-
Here is an example from the console log while I was resetting the error ` Ethernet: not installed ## Mqtt reconnects: 15 ## Correct data: 99.64% Rules active: 3Fri Dec 6 09:49:32 2024 (1405261279): Requesting new panasonic data |
Beta Was this translation helpful? Give feedback.
All reactions
-
There is isolated command ( in ProtocolByteDecrypd.md , at the end) from beginning , to do this ( the same command ,with reboot HP) , but it was decided not to implement it... But first i would focus on Error H23 it self . It is the error of sensor ,with reads the parameter called in Heishamon TOP51 Inside_Pipe_Temp. Maybe it is something wrong with it ? It not fit properly ( then measure something else what it should). |
Beta Was this translation helpful? Give feedback.
All reactions
-
I don't think this is the case with my device. As I understand it, the temperature pattern looks correct. |
Beta Was this translation helpful? Give feedback.
All reactions
-
-55° ?!? Is'nt it too low? |
Beta Was this translation helpful? Give feedback.
All reactions
-
Exactly. That's why H23 is thrown. |
Beta Was this translation helpful? Give feedback.
All reactions
-
And true temperature is? Have you measured it? You could attach some dallas temperature sensors in parallel.. also it would be great to measure it's resistance.. |
Beta Was this translation helpful? Give feedback.
All reactions
-
Yes, I measured it with an external temperature probe I attached to the pipe. Readings were identical (but this defrost cycle only went down to -24 °C) |
Beta Was this translation helpful? Give feedback.
All reactions
-
Additionally , it was decided not to implement it exacly for the reason you want to do it ! |
Beta Was this translation helpful? Give feedback.
All reactions
-
👍 1
-
I basically agree with you. |
Beta Was this translation helpful? Give feedback.
All reactions
-
You can use at the end SendRawValue command.... EDIT: And please remember , to switch HP to off ( with SetHeatpump =0 command ) and wait some seconds , then do the reboot). |
Beta Was this translation helpful? Give feedback.
All reactions
-
OK, thanks. However, I have since been informed that it also works using the “http://192.168.XXX.XX/command?SetReset=1” restapi command. Thanks anyway |
Beta Was this translation helpful? Give feedback.
-
Is it possible to add the “Error reset” switch?
Some Leisha have the problem with error H23 and then the heat pump switches off and goes into fault mode.
At the moment there are only two ways to get the pump running again.
Either directly on the heat pump terminal or in the Panasonic Service Cloud.
Therefore, it should also be possible to implement this function in Heishamon, which allows the option of a script to work around the problem.
best regards
rubinho