heat flux limit and its measurement #13775

Answered by drjfloyd
fr-evtech asked this question in Q&A
Discussion options

You must be logged in to vote

I would not use the integrated intensity.
One option is a sensor pointed at the fire and one at the ceiling and then take the vector sum of the two. (see Chap 66 of the SFPE Handbook).
Another option is multliple sensors pointing along the arc from the fire to the ceiling and picking whichever is the highest at any timestep.