USB2RS485 question + 2-speed pump question #238

Answered by sfeakes
Sazerak asked this question in Q&A
Discussion options

You must be logged in to vote

From your description, it doesn’t sound like AqualinkD will work for your setup. AqualinkD communicates directly with a Jandy control panel. While AqualinkD can read messages from all RS485 devices it does not control them directly. Each RS485 bus needs a master device, (their can only be one master) and that controls communication with every other device on the bus. This master is the control Jandy panel. So unless you have a Jandy control panel that you have not mentioned above, AqualinkD will not work.

Their are other projects out their that can act as a master device for Pumps and SWG, but none that I know of for JX(i) heaters. At some point in the future I’ve always imagined creating…