Controlling a SuperFlo VS directly with GPIO instead of relays - configuration questions #960

Answered by tagyoureit
EgonSpengler asked this question in REM
Discussion options

You must be logged in to vote

My main problem: the circuits are not treated as mutually exclusive - selecting one speed should disable the others, but they all stay where toggled manually (I assume my triggers in REM are to blame here?)

I just took a quick look at our logic and the pump manuals. The pump can accept multiple, simultaneous inputs and it will default to the highest priority. There is no expectation by the pump or our code for mutual exclusivity.

Per the manual:

Note: If more than one input (switch) is present, then the pump will give priority to the highest number input. Therefore OVERRIDE has highest priority followed by STEP 3, then STEP 2, then STEP 1.

In your setup, the priority at the pump side …